Kieth,

I have an off grid VFX3648 out in the field and the customer reports it 
occasionally faults starting their 1 HP well pump, so I feel this is 
pushing the limit of the inverter. There is NO WAY a single (or even 
stacked double) inverter will start a 3 HP well pump unless it is a no 
surge pump like Grundfos makes.

Todd


Keith Cronin wrote:

> Hello
>
>
>
> What is the best method for addressing the challenge of starting a 3hp 
> motor
> with an outback 3048?
>
>
>
> The specs say it can handle 70 amps peak ac for 1msec and 50 amps surge 
> RMS
> for 100msec
>
>
>
> What is the biggest motor you folks have started and kept running with 
> an
> OB3048 with turbo?
>
>
>
> Anyone want to chime in would be appreciated.
>
>
>  
>


- - - -