Outback 3048 with turbo [RE-wrenches]
Darryl Thayer
daryl_solar at yahoo.com
Sat May 5 10:30:25 PDT 2007
Hi Keith and Don
It depends very strong what the mechanical load is
connected to the motor. Is there a way to unload the
motor?
At start up you have locked rotor current, which is
deminished as the motor starts to spin. The locked
rotor current on some of the motors I have worked with
is about 6 times running current. It is higher for
high efficiency motors. The locked rotor current
varies with motor design.
Wild guess here, but I would try a reduced voltage
start, with minimum mechanical load. The reduced
voltage can be attained by double contactors and
connecting to both low voltage and high voltage
windings. See Don's question below.
Darryl
--- Don Loweberg <I2P at aol.com> wrote:
> kcronin at islandenergy.net writes:
>
> What is the best method for addressing the challenge
> of starting a 3hp motor
> with an outback 3048?
> What voltage?
____________________________________________________________________________________
Food fight? Enjoy some healthy debate
in the Yahoo! Answers Food & Drink Q&A.
http://answers.yahoo.com/dir/?link=list&sid=396545367
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list