A Colorado inspector told me to size the feeder for the load. He stated that performance issues were between the customer and myself. Different inspectors might have a different take on this. Certainly head room should be left for future expansion.
On long runs, I'm in favor of running conductors in parallel. You will use less metal to achieve the desired VD, and the pulling will be a lot easier.
-Drake
----------------------------------------
From: William Miller <wrmiller at charter.net>
Sent: Thursday, January 04, 2007 10:37 AM
To: RE-wrenches at topica.com
Subject: Long residential feeder [RE-wrenches]
Colleagues:
I wanted to see if there is a consensus on the subject of sizing long
residential feeders. I have some off-grid jobs coming up with feeders
anywhere from 350 to 530 conduit feet and I need to specify feeder
sizes. Here's the philosophy I have been using, I'd be curious if anyone
disagrees:
NEC 215.2 A (4) specifies feeders to not exceed 3% VD. I agree this is
appropriate for considering VD for the maximum draw I might
expect. Furthermore, I imagine that peak current draw will occur
infrequently (or these customers are going to exceed the capability of
their systems on a regular basis).
I base my calculations on a maximum draw of 50 amps for the larger off-grid
residences I am now designing for. If the VD approaches 3% at 50 amps, it
is not much above 1% for 30 amp draws. I figure staying in this range is safe.
Comments from this group are always greatly appreciated.
William Miller
__________________________________________________________________
William Miller
Miller Power and Communications
Voice :805-438-5600 Fax: 805-438-4607
email: wrmiller at mpandc.com
http://mpandc.com
License No. C-10-773985
_____________________________________________________________
Check out our latest project at
http://mpandc.com/case_studies/pv_school/pv_school.html
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
[Non-text portions of this message have been removed]
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list