Long residential feeder [RE-wrenches]
Ray Walters
walters at taosnet.com
Fri Jan 5 17:26:02 PST 2007
<x-flowed>
We use Aluminum URD direct burial for long AC runs; the price just can't
be beat. Much easier than conduit over 200 ft. When sizing, I also look
at volt drop during starting surges for pumps, power tools, etc. to make
sure I'm not dropping below the minimum voltage allowed for the
particular device. I usually keep it below 6%, though some things can
stand a drop to 10% for a couple of seconds.
We just ran 2000 ft for a well pump, voltage at startup at the pump was
235 vac (from pair of SW 4024s), while the generator used previously at
the well head wa s dragging down to 210 vac.
Ray
>
>
>
>A Colorado inspector told me to size the feeder for the load. He stated that performance issues were between the customer and myself. Different inspectors might have a different take on this. Certainly head room should be left for future expansion.
>
>
>
>On long runs, I'm in favor of running conductors in parallel. You will use less metal to achieve the desired VD, and the pulling will be a lot easier.
>
>
>
>-Drake
>
>
>
>----------------------------------------
>
>
>
> From: William Miller <wrmiller at charter.net>
>
>Sent: Thursday, January 04, 2007 10:37 AM
>
>To: RE-wrenches at topica.com
>
>Subject: Long residential feeder [RE-wrenches]
>
>
>
>Colleagues:
>
>
>
>I wanted to see if there is a consensus on the subject of sizing long
>
>residential feeders. I have some off-grid jobs coming up with feeders
>
>anywhere from 350 to 530 conduit feet and I need to specify feeder
>
>sizes. Here's the philosophy I have been using, I'd be curious if anyone
>
>disagrees:
>
>
>
>NEC 215.2 A (4) specifies feeders to not exceed 3% VD. I agree this is
>
>appropriate for considering VD for the maximum draw I might
>
>expect. Furthermore, I imagine that peak current draw will occur
>
>infrequently (or these customers are going to exceed the capability of
>
>their systems on a regular basis).
>
>
>
>I base my calculations on a maximum draw of 50 amps for the larger off-grid
>
>residences I am now designing for. If the VD approaches 3% at 50 amps, it
>
>is not much above 1% for 30 amp draws. I figure staying in this range is safe.
>
>
>
>Comments from this group are always greatly appreciated.
>
>
>
>William Miller
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list