Colleagues:
I wanted to see if there is a consensus on the subject of sizing long
residential feeders. I have some off-grid jobs coming up with feeders
anywhere from 350 to 530 conduit feet and I need to specify feeder
sizes. Here's the philosophy I have been using, I'd be curious if anyone
disagrees:
NEC 215.2 A (4) specifies feeders to not exceed 3% VD. I agree this is
appropriate for considering VD for the maximum draw I might
expect. Furthermore, I imagine that peak current draw will occur
infrequently (or these customers are going to exceed the capability of
their systems on a regular basis).
I base my calculations on a maximum draw of 50 amps for the larger off-grid
residences I am now designing for. If the VD approaches 3% at 50 amps, it
is not much above 1% for 30 amp draws. I figure staying in this range is safe.
Comments from this group are always greatly appreciated.
William Miller
__________________________________________________________________
William Miller
Miller Power and Communications
Voice :805-438-5600 Fax: 805-438-4607
email: wrmiller at mpandc.com
http://mpandc.com
License No. C-10-773985
_____________________________________________________________
Check out our latest project at
http://mpandc.com/case_studies/pv_school/pv_school.html
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list