Paralleling Battery Banks [RE-wrenches]

Darryl Thayer daryl_solar at yahoo.com
Sat Dec 30 06:35:35 PST 2006


Unless the run is extra long I would not parallel the
home runs but be sure each battery set sees exactly
the same copper run.  and make a few cross ties.
darryl
--- Walt Ratterman <wratterman at SunEnergyPower.com>
wrote:

> 
> 
> Quick Question:
>  
> We have a remote situation, where we have two sets
> of 48V "Batteries"
> comprised of 24-2V cells each, to be part of an
> Outback Power system.
> We are running two sets of 4/0 home run cables back
> to the inverter.
> One set will be from each of the two 48V battery
> banks.
>  
> Normally, we would parallel the two batteries at the
> battery location
> (as well as having them paralleled where the homerun
> cables come into
> the inverter).  
>  
> We are facing a situation where we may be short on
> battery cables.  Do
> you see any particular problem in leaving off the
> paralleling cables at
> the battery bank, and having the paralleling done
> only where the homerun
> cables come together in the Inverter enclosure?
>  
> Thanks,
>  
> Walt Ratterman
> Rwanda
> 
> [Non-text portions of this message have been
> removed]
> 
> 
> - - - -
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
> 
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
> 
> Check out participant bios:
> www.mrsharkey.com/wrenches/
> 
> Hosted by Home Power magazine
> 
> Moderator: michael.welch at homepower.com
>
> 
> 
> 


__________________________________________________
Do You Yahoo!?
Tired of spam?  Yahoo! Mail has the best spam protection around 
http://mail.yahoo.com 


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-wrenches mailing list