Outback with Sunnyboy [RE-wrenches]
Jonathan Hill
solarjon at sierrasolar.com
Tue Dec 5 17:16:43 PST 2006
<x-flowed>
>Jonathan Hill wrote:
>> Will the entire array output continue to charge the batteries through
>> the OutBack's even if it exceeds the OutBack's rating?
>
>Only until the OutBack's get too hot and shut off. If AC loads are
>running at the same time it will reduce this from occurring.
>
>All of the systems we have done have had about even amounts of grid-tie
>and battery based inverters - i.e. if there was 8 kW of SunnyBoy then
>there was at least 8 kW of OutBack inverters...
>
>There are ways to configure a system to prevent overloading the
>OutBack's if they had to be less - basically you can have a dump load
>turn on the burn up the excess power on the AC side of the system -
>between the batteryless gridtie and the OutBacks.
>
>Dave Katz's comment about providing a way to shut off the batteryless
>grid-tie inverter when the battery is full was correct - although I
>prefer to use a dump load system which diverts the excess power to a
>useful purpose instead. This has varried from using some old C40
>controllers to multiple solid-state relays. The SSR give the option of
>dumping the excess to either AC or DC loads.
>
>Christopher Freitas
>OutBack Power Systems, Inc.
>cfreitas @ outbackpower.com
>www.outbackpower.com
>Arlington WA USA
>Tel 360 435 6030
>
Chris-
If that's the case, why not just use the Outbacks and skip the Sunnyboys?
Jon
--
-----------------
Sierra Solar Systems
563C Idaho Maryland Road
Grass Valley, CA 95945
tech info and foreign orders: (530) 273-6754
order line: (888) ON-SOLAR (US only) FAX: (530) 273-1760
e-mail: <mailto:solarjon at sierrasolar.com>
world wide web: <http://www.sierrasolar.com>
Because of the high volume of e-mail to which I respond, please
leave _all_ of the previous messages (unless it's unbearable) in
your reply so I can better remember your original message.
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list