Branch circuits in Subpanels [RE-wrenches]
Jeff Clearwater
clrwater at earthlink.net
Tue Oct 31 04:02:52 PST 2006
<x-flowed>
Hi Dan,
Reason Prevails!
Thanks,
Jeff C.
Village Power Design
>Steve et. al.
>
>With all due respect, 312.8 says "Enclosures for switches or
>overcurrent devices
>shall not be used as junction boxes, auxiliary gutters, or raceways for
>conductors feeding through or tapping off to other switches or overcurrent
>devices, unless adequate space for this purpose is provided. The conductors
>shall not fill the wiring space at any cross section to more than 40
>percent of
>the cross-sectional area of the space, and the conductors, splices, and taps
>shall not fill the wiring space at any cross section to more than 75
>percent of
>the cross-sectional area of that space."
>
>Splices are specifically allowed under the conditions specified, wire nuts
>included.
>
>Dan Rice
>Abundant Sun, LLC.
>
>Quoting Steve Lyons <sinepv at hotmail.com>:
>
>>
>> Hi Geoff!
>>
>> Please see 2002 NEC Art. 312.8 " Enclosures for Switches or Overcurrent
>> Devices".
>> The first sentence says it all " Enclosures for switches or overcurrent
>> devices SHALL NOT be used as junction boxes".
>>
>> During my 30+ years as a journeyman, I have seen breaker panels with wire
>> nuts and taped split bolt splices, it is not goog practice or acceptable.
>>
>> We all should know the NEC requirements as well as we do the solar.
>>
>> Hope this helps.
>>
>> Stephen Lyons
>> Sine Electric
>> C-10 & General Journeyman Electrician
>> 324 Grandview Avenue
>> Novato, CA 94945
>>
>> sinepv at hotmail.com
>>
>> >From: Geoff Greenfield <Geoff at Third-Sun.Com>
>> >Reply-To: RE-wrenches at topica.com
>> >To: RE-wrenches at topica.com
>> >Subject: Re: Branch circuits in Subpanels [RE-wrenches]
>> >Date: Mon, 30 Oct 2006 15:23:02 -0500
>> >
>> >
>> >Has anyone ever been hassled about having wire nuts in a load center? A
>> >local inspector we had a pre-job plan review with told us that the load
>> >center is not listed as a junction box. He said we had to pull the romex
>> >out and splice extensions to the new sub panel.
>> >
>> >For a brighter energy future,
>> >
>> >Geoff Greenfield
>> >NABCEP Certified Energy Practitioner
>> >
>> >THIRD SUN SOLAR & WIND POWER Ltd.
>> >340 West State Street
>> >Athens, OH 45701
>> >
>> >www.third-sun.com
>> >(740) 597-3111
>> >
>
>
>
>----------------------------------------------------------------
>SCI WebMail http://webmail.scinternet.net/
>
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & how to change your email address:
>www.mrsharkey.com/wrenches/etiquette.php
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
--
~~~~~~~~~~~~~
Jeff Clearwater
Village Power Design
Sustainable Energy & Water Solutions for Home & Village
http://www.villagepower.com
gosolar at villagepower.com
NABCEP (tm) Certified Solar PV Installer
530-470-9166
877-SOLARVillage
877-765-2784
65 Schoolhouse Rd
Amherst, MA 01002
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~`~
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list