battery box venting flow rate? [RE-wrenches]
Mike Kocsmiersky
mikek at KosmoSolar.com
Wed Sep 20 05:26:31 PDT 2006
Joel & Kirk,
If I recall IBE battery put out that venting formula that Joel references
and is a good rule of thumb. Also, Concorde Battery has some data for their
sealed batteries. It all boils down to keeping the concentration of
hydrogen to less than 2%. This will be a function of charging, gassing rate
of particular battery, and volume of the battery container or room; I
typically never rely on passive ventilation especially for a battery
container, because as John Wiles was stating you could get exterior forces
pressuring the air back into the container. I typically use Joel's formula
and actively vent to the outside. Its also not uncommon to put in a
secondary active vent as a safety, or a hydrogen concentration sensor when
dealing with larger battery rooms. As Joel's calculations show, it is
typically a small amount of ventilation.
Mike Kocsmiersky
President
Kosmo Solar
(413) 734-1456
-----Original Message-----
From: Joel Davidson [mailto:joeldavidson at earthlink.net]
Sent: Tuesday, September 19, 2006 8:44 PM
To: RE-wrenches at topica.com
Subject: Re: battery box venting flow rate? [RE-wrenches]
Kirk,
Battery rooms must be properly vented to prevent the build-up of potentially
explosive hydrogen gases released during charging. The correct charge
controller and charge settings will limit out-gassing during normal
charging. However, topping off and equalization charging, requirements for
long battery life, will produce hydrogen. Concentrations of 4% hydrogen are
explosive. 2% is the recommended maximum concentration for battery storage
areas. Use the following formula to determine the size of your battery room:
Q = 0.0135 x I x N
Q is the necessary quantity of air ventilation in cubic feet per minute
(CFM).
I is the charge rate in amperes.
N is the number of series connected cells.
For example, a PV system with eight 100 watt modules (rated 17.1 V, 5.88 A)
and sixteen 6-volt batteries is wired for 24 volts DC. The required venting
is 0.0135 x (5.88 x 4) x 12 = 3.81 CFM or 228.6 cubic feet per hour. Many
rooms are 8 feet in height with 2 air changes per hour. A room 8' x 6' x 6'
has 288 cubic feet volume and naturally vents 576 cubic feet per hour,
almost 2.5 times the required 288.6 cubic feet per hour.
Joel Davidson
----- Original Message -----
From: "Kirk Herander" <kirk at vtsolar.com>
To: <RE-wrenches at topica.com>
Sent: Tuesday, September 19, 2006 8:37 AM
Subject: battery box venting flow rate? [RE-wrenches]
>
>
> Hello,
>
> Is there any minimum airflow/cfm recommended to safely power vent a
> battery box?
>
> Kirk Herander
> Vermont Solar Engineering
> 802.863.1202
> fax 802.863-7908
> NABCEP(tm) Certified Solar PV Installer
> Xantrex Certified Dealer Charter Member
> NYSERDA-eligible installer
> VT Solar and Wind Partner
>
>
> _____
>
> I am using the free version of SPAMfighter for private users.
> It has removed 29354 spam emails to date.
> Paying users do not have this message in their emails.
> Try SPAMfighter <http://www.spamfighter.com/go.asp?t=249> for free now!
>
>
> [Non-text portions of this message have been removed]
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list