*** SPAM *** RE: Outback FX voltage fun [RE-wrenches]
Darryl Thayer
daryl_solar at yahoo.com
Fri Sep 8 07:46:41 PDT 2006
Hugh
This sounds like a surge problem. In many situations
we have motors and heavy inductive loads starting and
stoping, this puts surges on the line. The only
difference is yours happens every cycle. The energy
surge per cycle does not sound very high, but the
repetive nature will increase the power to be dispated
by the surge arrester. Perhaps an industrial (400
volt MOV or the other type) arrestor could tame the
surge voltage.
Darryl
--- Hugh Piggott <hugh at scoraigwind.co.uk> wrote:
>
> thanks Chris,
>
> > Effectively - The OutBack charger is sending the
> power
> >from the generator to the battery - but since the
> battery is so "stiff"
> >some of the energy gets reflected back at the
> generator. Often the
> >response time of the generator's voltage regulator
> is fairly slow - so
> >the AC output voltage of the generator jumps up
> since there is nowhere
> >for the power to flow.
>
> I guess this is an inductive spike due to suddenly
> switching off the current.
> >
> >
> >The two solutions I have used with issues like this
> on OutBack and other
> >inverters is to add some HV motor run capacitors
> (20 to 50 mF) across
> >the AC output of the generator itself or to ensure
> that there is a
> >resistive load on the generator when the charger is
> running.
>
> OK thanks I'll try a 20 uF cap next time and I will
> put a water
> heater on as well. It may be a while before I get
> around to it -
> depends on the wind.
>
> All the best,
>
> --
> Hugh
>
> Scoraig Wind Electric
> http://www.scoraigwind.co.uk/
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios:
> www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
>
__________________________________________________
Do You Yahoo!?
Tired of spam? Yahoo! Mail has the best spam protection around
http://mail.yahoo.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list