thanks Chris,
> Effectively - The OutBack charger is sending the power
>from the generator to the battery - but since the battery is so "stiff"
>some of the energy gets reflected back at the generator. Often the
>response time of the generator's voltage regulator is fairly slow - so
>the AC output voltage of the generator jumps up since there is nowhere
>for the power to flow.
I guess this is an inductive spike due to suddenly switching off the current.
>
>
>The two solutions I have used with issues like this on OutBack and other
>inverters is to add some HV motor run capacitors (20 to 50 mF) across
>the AC output of the generator itself or to ensure that there is a
>resistive load on the generator when the charger is running.
OK thanks I'll try a 20 uF cap next time and I will put a water
heater on as well. It may be a while before I get around to it -
depends on the wind.
All the best,
--
Hugh
Scoraig Wind Electric
http://www.scoraigwind.co.uk/
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list