Concentric knockouts on circuits over 250 volts [RE-wrenches]
Mark Frye
markf at berkeleysolar.com
Mon Aug 28 08:12:49 PDT 2006
The interesting thing to me is the issue of UL listings. If I buy a
600V DC rated disconnect from my supply house, and ask them to give me a
copy of the UL listing information, he laughs me out the store and askes
for the next cash carrying customer.
In any event, I do not bond my DC conduits. It seems pretty clear that
250.97 contains it's own exception on this issue:
"250.97 (c) Fittings with shoulders that seat firmly against the box or
cabinet, such as electrical metallic tubing connectors, flexible metal
conduit connectors, and cable connectors, with one locknut on the inside
of boxes and cabinets"
Since I use EMT for my conduit run and I use "electrical metallic tubing
connectors" wtih one locknut on the inside of the box, I rely on 250.97
itself to exempt me from bonding the conduit.
Mark Frye