Outback VFX with GFCI [RE-wrenches]
Christopher Freitas --- OutBack Power
cfreitas at outbackpower.com
Tue Aug 15 16:32:09 PDT 2006
Very good point Allan - I know that there are smoke detector systems
with back-up batteries in them as well which might be a solution to this
search mode problem.
Search mode is a bit "over-rated" as you can usually add another module
and eliminate the hassle. Obviously an expensive solution but as a
portion of the total system cost its fairly low. Just be sure to keep
the phantom loads off still.
Search mode will still have its uses - such as when there is an inverter
dedicated to power some separate large load such as a well pump that
runs infrequently.
Most of the issues we see with GFCI end up being an error in the wiring
of the system - causing a - you guessed it - ground fault!
Christopher
Allan Sindelar wrote:
>
> Kelly,
> The concern I would have is not with GFCIs but with smoke detectors.
> They
> must be wired such that if one alarms they all do. If the inverter is
> able
> to sleep, this would not occur. My fear is that in the event of a fire,
> you
> as installer could be liable for consequences.
>
> I have never seen anything in print about this, so it may be an
> unsubstantiated fear. But the day may have arrived when we can't allow
> inverters to sleep for reasons of liability.
>
> I would be interested in others' take on this.
>
> Allan at Positive Energy
>
> ----- Original Message -----
> From: "Kelly Larson" <solarwrench at asis.com>
> >
> > I am wiring a new off-grid house and wonder about search mode and
> > GFCI/AFCI receptacles and breakers. The customer is old school and
> > wants the minimum energy use possible. (Can you believe there are still
> > customers like that out there?)
> >
> > Has anyone run standard NEC wired house with GFCI/AFCI receptacles and
> > breakers and gotten the VFX into the search mode? Any ideas how much
> > these receptacles and breakers use? Different wiring approaches for
> > minimum electricity use?
> >
>
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list