Andrew,
Nope, if it has a 200A main breaker; 40A is all you get. If you put in a
175A main breaker, OK.
Allan
----- Original Message -----
From: "Andrew Truitt" <atruitt at gmail.com>
>
> Is it legit to backfeed a 200 amp main panel with the 1 pole, 60 amp
> breaker that is recommended for the Outback FXGT 3048 considering the
> 20% rule? I know that most of that amperage is pass through, as the
> most a 3kW inverter should be able to produce at 120V is 25 amps, but
> the manual says that the largest instantaneous output current is 70
> amps.
>
- - - -