Backfeeding a 200 amp panel with an Outback 3048 [RE-wrenches]
Andrew Truitt
atruitt at gmail.com
Wed Oct 11 13:48:52 PDT 2006
<x-flowed>
Do you mean 275A?
On 10/11/06, Allan Sindelar <allan at positiveenergysolar.com> wrote:
>
> Andrew,
> Nope, if it has a 200A main breaker; 40A is all you get. If you put in a
> 175A main breaker, OK.
> Allan
>
> ----- Original Message -----
> From: "Andrew Truitt" <atruitt at gmail.com>
> >
> > Is it legit to backfeed a 200 amp main panel with the 1 pole, 60 amp
> > breaker that is recommended for the Outback FXGT 3048 considering the
> > 20% rule? I know that most of that amperage is pass through, as the
> > most a 3kW inverter should be able to produce at 120V is 25 amps, but
> > the manual says that the largest instantaneous output current is 70
> > amps.
> >
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
--
Andrew Truitt
System Designer
Standard Solar Inc.
(301) 296 - 4373
andrewtruitt at standardsolar.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list