Battery strings [RE-wrenches]
Ray Walters
walters at taosnet.com
Mon Sep 18 10:26:13 PDT 2006
<x-flowed>
Hi Bob;
I've recently gone to single strings, but had one bad cell (Rolls) take
out the whole system. My current thinking is that 2 string designs are
the best compromise between limiting parallel problems without single
string problems.
Also, related to this: I have a question on how folks are wiring up
large battery banks and multiple inverters. How many 4/0 cables are
going to the batteries from the busbar for say a 12 Ouback inverter
system? Trace used to use the same cable and just jump from one inverter
to the next. I figured they could do this because of the out of phase
relationship between the inverters. (DC to an inverter is not really
DC.... just check with an oscilloscope)
So where is the rule book for battery cable sizing on multiple inverter
systems?
Thanks ya'll
Ray Walters
Chris Worcester wrote:
>Hi Bob,
>
>If you want to use a bus bar assembly I hooked up 10 VFX3648's to 2 strings
>of Rolls 2-KS-33's using Ilsco insulated 4/0 x 14 port splice taps/bars.
>This is a really neat way to do a 4/0 bus bar. They make these
>splicer/reducers from two hole to 14 hole. They were around $270 for the
>pair and well worth it.
>
>Sincerely,
>
>Chris Worcester
>NABCEP Certified PV Installer
>USA Distributor of Proven Wind Turbines
>Toll Free: 877-682-4503
>Fax: 530-582-4603
>www.solarwindworks.com
>chris at solarwindworks.com
>"Proven Energy Solutions"
>-----Original Message-----
>From: Bob Ellison [mailto:ellison at gisco.net]
>Sent: Friday, September 15, 2006 2:09 AM
>To: RE-wrenches at topica.com
>Subject: Battery strings [RE-wrenches]
>
>
>
>I am putting together a pack of 12 L-16's @ 24 volts and am wondering if
>there is a definite opinion on what works better, connecting at the corners
>of the pack or running each string to it's own buss bar and from there to
>the inverter.
>I have seen failures of the major positive and negative when corner
>connected. I assume from the all the banks current running through the
>connections. I have also heard suggestions to rearrange the battery bank
>during it's life. (too much like work)
>Has anyone had better luck with each string going to a bus bar then to the
>inverter? Similar to the "big buss" that Outback used to make?
>
>Thanks,
>Bob
>
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: mwelch at redwoodalliance.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bXdlbGNo
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list