If you really want to reset the chF alarm manually:

Press and hold the Select button until you get to the historical data.  Tap
the Select button until you get to DSC (days since charged).  Press and hold
Reset until the number resets to 0.

However, the alarm is an warning for a reason.  If inaccurate programming is
causing this problem, fix the programming.  If caused by inadequate charging
capability or too short charge times, "fixing" the problem by resetting the
alarm is like driving your car with duct tape over the gauges to keep from
being annoyed by that pesky low oil light.

Batteries need to be charged to truly full at least once a week.  If the
customer is not achieving this, what is the cause?  Is the charging source
going to float but the meter not resetting?  If so, are the inverter charger
settings adequate?  Or are the TM settings too conservative?  Or is the
customer not allowing the generator to fully charge the batteries (200a
charging into 3500ah = a heck of a lot of genny runtime)

For setpoints for this situation, I would begin with 14.4, 70a, 95-96H, PO1,
3,000-3,500ah, 7dSC, 90dSE, 11bLO.


 
Phil Undercuffler ext.238
Technical Support
phil at dankoffsolar.com

Dankoff Solar Products
    
The Premier Manufacturer and Distributor of Solar Water Pumps, and
Wholesale Distributor of Solar Electric, Wind, and Solar Heating Equipment

888-396-6611 toll free
505-473-3800 phone
505-473-3830 fax
www.dankoffsolar.com




on 1/6/05 2:15 PM, k la at SolarWrench at yahoo.com wrote:

> I was looking for a way to reset the Trimetric chF alarm (flashing lights)
> without unplugging the meter (and loosing the collected data).  Anyone figure
> out how to do this?
> 
> 
> 
> What voltage/current setpoints are used in a system with a big bat bank and
> only gen charging?  This particular bank is a 3500AH at 12V, (I know, I didn't
> install it), and is capable of charging at 200A max.
> 
> Kelly Larson

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
How about a cruise on your favorite cruise line-from us?  Click 
here.
http://click.topica.com/caac2NYbz8Qcsbz9JC9f/PermissionData
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------






More information about the RE-wrenches mailing list