Top of pole internal wiring [RE-wrenches]
Darryl Thayer
daryl_solar at yahoo.com
Wed Dec 14 23:51:50 PST 2005
HI Gary
Some of te approaches I have used is to drill and tap
with a 1" pipe tap and put a "chase nipple" through
the back of the box into the pole. Or Screw in a 90
degree seal tight connector. If the top of the pole
is open more elaborate solutions are possible.
Darryl
--- Gary Higbee <gary at windstreamsolar.com> wrote:
> Wrenches,
>
> What is the best way to exit wires from inside a top
> of pole PV mount? I've
> got a park project, and they don't want a conduit
> run up the side of the
> pole (concerns someone will break it--this is a
> vandalism-prone area). We'll
> have three runs of #6 coming up the inside of a 6"
> schedule 80 pole. The
> 7/8" hole in the DP&W TOP mount will only take a
> 1/2" fitting, but we need
> 1" conduit for the three #6's. If we drill a hole
> through the pole wall we
> can't use nonmetallic flex out the side, because the
> bend radius is too
> small.
>
> We'll be combining two strings of four Unisolar
> ES-62's in a J-box up there.
> What's the best way to get from the inside of the
> pole to the box?
>
> Thoughts?
>
> Thank you!
>
> Gary
>
> ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~