"An inverter cannot be run off an inverter"? Why not? I am SURE a SQ
could be run off an Outback FX. It is way too clean of a sinewave to
cause any problems. The SQ's electronics wouldn't know the difference.
A followup on the 2500 amp hour 12 volt dual DR1512 inverter / pump
issues. Once I finally got the batteries fully charged (they were pretty
dead) the DR's amazingly manage to groan that 1.5 HP to life. Running
amps (DC) were 205 @ 12.3 volts! That is over 2500 watts to run about
1200 watts worth of pump! Some serious inefficiencies going on there.
I'd like to meet and talk with the guy that designed that system! How I
hate cleaning up other people's messes... and yes I did suggest to the
homeowner they consider a 3/4 HP pump.
On another note, does anyone else run into gigantic well pumps on off
grid systems? I think the well drillers must make more money on bigger
pumps or something. I have seen several systems (that I did not do)
where the folks had to start their generator every time they wanted to
fill up their pressure tank because the inverter(s) could not start the
pump. Sheesh! Unless you are irrigating a pasture or something, 3/4 HP
is plenty.
Todd
Matt Tritt wrote:
> Hi Travis,
>
> Just to flog this dog a little more, a few years back I had a
> completely confusing talk with the the head "engineer" at (the now
> defunct) Hayes Pump about running their "constant pressure" pump with
> an SW; something way better than a DR presumably, but still with not
> that many steps per wave. I was finally informed that it couldn't be
> done because their pump has some kind of inverter actually built into
> the motor housing. His logic was "you can't run an inverter with an
> inverter". How he knew this to be the case, I have no idea - and he
> might have been just guessing.
>
> Assuming that the SQ and SQE also have use something similar to make
> variable speed possible with a 240 VAC pump motor, I would assume that
> my suggestion to use one of these pumps with a pair of DRs is pretty
> lame. Rats. I also hate it when I'm wrong.
>
> On the other other hand, I bet the system in question would work fine
> if they could simply change to a conventional 3/4 HP pump.
>
> Matt T
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Need Emergency Cash? Get Up To $500 Now!
No Credit Checks, Easy & Fast Approval
Cash in you account Overnight!
http://click.topica.com/caadOurbz8Qcsbz9JC9f/911PaydayAdvance
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list