hybrid grid tie [RE-wrenches]
Bill Brooks
billb at endecon.com
Wed Feb 11 10:18:46 PST 2004
Keith,
My remark on code compliance deals with listed equipment. I am unaware of
any dc-to-dc converters that are listed. Using an Outback inverter with a
SunnyBoy on its subpanel side is unlikely to be a listed application for
that inverter, regardless of how well it works. If the inspector checks off
on it, I guess you're okay--but it would be more out of ignorance than
having fully understood your application and approved it. Ultimately it is
your call and whether the inspector will okay it.
Bill.
-----Original Message-----
From: Keith Cronin [mailto:sales at islandenergy.net]
Sent: Tuesday, February 10, 2004 10:19 PM
To: RE-wrenches at topica.com
Subject: RE: hybrid grid tie [RE-wrenches]
Bill
What is the real code issue? As long as it is labeled per NEC 690.54,56,
what other code items should I be addressing? As long as I have
documentation/plaques depicting the system and having the blessing of
the AHJ, where is listing dilemma? As long as I address 690.64 and
clearly layout where I am connecting to the supply side of the service
disco, there shouldn't be a problem.
If Chris and John or any of the manufacturers reps see potential
pitfalls with this technique before the debut of the Sunny Island, I
would like to hear their views.
Thanks Bill and all!
Keith Cronin
President
Island Energy Solutions Inc
318A Kuulei Rd
Kailua, HI 96734
808-262-3268 Tel
808-263-0338 Fax
www.islandenergy.net
-----Original Message-----
From: Bill Brooks [mailto:billb at endecon.com]
Sent: Tuesday, February 10, 2004 1:16 PM
To: RE-wrenches at topica.com
Subject: RE: hybrid grid tie [RE-wrenches]
Keith,
Although these are very interesting technical discussions, I think you
are
faced with a very real code issue. Although the Outback unit may work
fine
in conjunction with an SMA inverter, I don't either are listed for that
type
of operation (Chris and John will be happy to correct me if I'm wrong).
When
the Sunny Island is available in the U.S., that situation will change,
but
until then, I think you are stuck. I think the best code-compliant way
out
of this mess is the previous suggestion of using the Outback MPPT charge
controller with a slightly higher voltage array (3, 24V modules in
series)
and some huge wire.
If the code is not an issue--go nuts--but remember this guy has a lot of
money to pay lawyers.
Bill.
-----Original Message-----
From: Marco [mailto:marco at pvthawaii.com]
Sent: Tuesday, February 10, 2004 11:00 AM
To: RE-wrenches at topica.com
Subject: RE: hybrid grid tie [RE-wrenches]
A number of years ago I purchased a device called a "Solar Maximizer"
from a
company in Australia, AES or AEI, I think.
****Buzz*** not listed--sorry--thanks for playing
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list