Hi Jeff,
I've seen this problem with Surrettes before. They have a different
electrolite solution so they charge differently.
Had a customer who took meticulus notes, ( on some big Rolls) and could
never get them to come right on the hydrometer or volts. Never got a good
response from Rolls either.
Also know of a number of dealers in my area who no longer carry
Rolls/surrette for the same problems you are having.
Couldn't say if the life or amp capacity isn't correct, but they do act
differently.
Curious about 1 thing. Why 16 batteries?
Thanks,
jay
Peltz Power
> I have an off grid client that has a 1.4 kW array, a 6.5 kW Kohler
> generator, and 16 Decca L-16 size 350 Amp-Hr batteries. System worked
> great for 5 years, although limited sun-hours due to being in bottom
> of a canyon!. He needed generator about 3 hours run time twice a
> week. Client recently decided to replace batteries and we supplied 16
> Rolls Surrette S460 batteries (350AH @ 20 hrs).
>
> Client cannot get these new batteries up to full charge. Nothing else
> changed in system, same solar input, same generator run time, same
> loads. He has tried setting his MPPT controller for equalize, then at
> end of day setting the Trace SW40 for equalize and running generator
> up to 6 hours. He has also tried to "fool" the inverter by resetting
> the bulk and absorption charge setpoints up to 30 volts to avoid the
> inverter shutting down the generator before a full equalize charge is
> complete (which is what it is doing now).
>
> He has monitored the charging progress by sp.gr. readings and Amp-hour
> meter and still can only reach a 75% full level. Nothing seems to get
> these even close to 100%. There are 2 batteries out of the 16 with
> sp.gr. staying slightly below the others, but since we cannot reach
> equalization, we cannot force the battery bank to balance.
>
> The old batteries did not have this problem and the owner is starting
> to feel the higher priced Surrette batteries are not as good as his
> older Decca L-16 batteries which he could re-charge to at least 90%
> full.
>
> We are thinking about dis-connecting the battery "strings" and
> charging only 8 at a time, but I do not want to do this each time an
> equalize charge is needed.
>
> Has anyone run into this before? Any other "tricks" to keep the
> inverter charging at full amps longer when powered from generator?
>
> Jeff Yago
>
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Should School Prayer be mandatory? Give us your opinion and win.
http://click.topica.com/caacDvTbz8Qcsbz9JC9f/PermissionData
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list