Colleagues:
I see this all the time, people do not understand fault paths. The code
citation is below. Section (2) is what applies if you wish to save the
cost of one conductor. Remember, the GROUNDED conductor is the "neutral",
the GROUNDING conductor is the "ground wire":
250.32 Two or More Buildings or Structures Supplied from a Common Service.
(A) Grounding Electrode. Where two or more buildings or structures are
supplied from a common ac service by a feeder(s) or branch circuit(s), the
grounding electrode(s) required in Part III of this article at each
building or structure shall be connected in the manner specified in
250.32(B) or (C). Where there are no existing grounding electrodes, the
grounding electrode(s) required in Part III of this article shall be installed.
Exception: A grounding electrode at separate buildings or structures shall
not be required where only one branch circuit supplies the building or
structure and the branch circuit includes an equipment grounding conductor
for grounding the conductive noncurrent-carrying parts of all equipment.
(B) Grounded Systems. For a grounded system at the separate building or
structure, the connection to the grounding electrode and grounding or
bonding of equipment, structures, or frames required to be grounded or
bonded shall comply with either 250.32(B)(1) or (2).
(1) Equipment Grounding Conductor. An equipment grounding conductor as
described in 250.118 shall be run with the supply conductors and connected
to the building or structure disconnecting means and to the grounding
electrode(s). The equipment grounding conductor shall be used for grounding
or bonding of equipment, structures, or frames required to be grounded or
bonded. The equipment grounding conductor shall be sized in accordance with
250.122. Any installed grounded conductor shall not be connected to the
equipment grounding conductor or to the grounding electrode(s).
(2) Grounded Conductor. Where (1) an equipment grounding conductor is not
run with the supply to the building or structure, (2) there are no
continuous metallic paths bonded to the grounding system in both buildings
or structures involved, and (3) ground-fault protection of equipment has
not been installed on the common ac service, the grounded circuit conductor
run with the supply to the building or structure shall be connected to the
building or structure disconnecting means and to the grounding electrode(s)
and shall be used for grounding or bonding of equipment, structures, or
frames required to be grounded or bonded. The size of the grounded
conductor shall not be smaller than the larger of
(1) That required by 220.22
(2) That required by 250.122
William Miller
At 07:46 AM 6/17/2004, you wrote:
>Geoff,
>If you check your NEC book I believe you'll find that all conduits carrying
>live circuits are required to include a ground wire and, since this is a
>split-phase system, it won't work so great without the neutral.
>
>Again, refer to your NEC for allowable wire sizing and any other questions
>you might have.
>Good luck.
>
>Matt T
-----------------------------------------------------------
Let University of Phoenix make 2004 your year. Evening,
weekend or FlexNet® classes over 130 locations. Look
into our programs and get the degree that gets you going!
http://click.topica.com/caaciq1bz8Qcsbz9JC9f/UOP
-----------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list