Matt Tritt wrote:
> When the generator powers down, there is a very noticeable transfer time 
> (with flickering) before the inverters take over. This was what was 
> happening when the inverter failed to begin with so we were a bit 
> nervous during testing. 

I have seen this with many different models of inverters - are you 
stopping the generator with the inverter's control or via the 
generator's control?  What often happens with large generators with good 
voltage regulators is that the generator spins to a stop in a ugly way - 
but it is able to keep the AC output voltage acceptable while spinning 
down.  The inverters have a hard time deciding if the generator is dying 
or is just having a hard time - but since the voltage is good, it stays 
connected longer than it probably should...

I've fixed this on a couple of systems by adding a contactor to the 
output of the generator - the contactor instantly opens when the 
generator is told to shut down - it can be wired into both the 
generators control panel and the remote autogenstart circuit as well 
usually.  With this contactor installed the shutdown/switchover were 
really sweet - I had to do this on all of the multiple SW series 
installations I was setting up a few years ago (the original QUAD 
configurations - a few of which are still running today - but were a 
huge amount of work to program and tune back then...).    

>The other thing has to do with the MX 60 apparently being involved with 
>some comm. error messages.  

This is not something I have encountered - so its hard for me to 
comment.  Your solution of isolating it from the HUB/MATE is probably 
the best approach (and it solved the problem) so I would stick with that 
for now.  I asked others here at OutBack if they had any ideas and will 
contact you off-list with any suggestions.  
 
> Many thanks to Outback again for all their help! I feel that any wrench 
> should feel comfortable in working with their equipment and their 
> technical service.

Thanks to you for sticking with us while we worked this out! 

Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com  
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030  

===========================================================
Your opinion counts! We’re conducting a survey for a 
computer service/repair company. When you complete our 
survey, you will also be entered into a drawing for one of 
ten $100 prizes. Just click
http://click.topica.com/caab8K1bz8Qcsbz9JC9f/ Val Rad
===========================================================
- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-wrenches mailing list