Hialeah KWH meter wiring diagrams [RE-wrenches]

Christopher Freitas --- OutBack Power cfreitas at outbackpower.com
Tue Feb 17 06:58:30 PST 2004


Ah - should have looked more before I posted - I found the diagrams:

http://www.hialeahmeter.com/diagrams.htm

The type of KWH meter which would be ideal is the form "12S" which is a 
5 jaw type.  

Using the "1S" type would not work as the pair of terminals for the 
neutral is simply a pass through and is not measured - so it will not be 
subtracted as required.  What we need is a 120/240 type "2S" meter but 
with a 120 vac voltage coil instead of a 240 vac coil.  

One of the "Polyphase" meters might also work instead.  Or I bet they 
could configure one to work correctly for our application.

Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com  
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030  

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------





More information about the RE-wrenches mailing list