Inverter Monitoring & Canceling Meter Legs [RE-wrenches]

Christopher Freitas --- OutBack Power cfreitas at outbackpower.com
Tue Feb 17 07:52:37 PST 2004


Geoff at Third-Sun.com wrote:
> I did connect the little screw to a neutral wire (after removing the 
> jumper) - some instructions I got told me to connect it to ground but I 
> was thinking that - minute as it is - the micro motor load would be 
> using the ground as a conductor.  Am I right in this thinking and 
> practice? If so we should heads up the suppliers who are recommending 
> this practice.

Yes - the tap should be connected to the neutral - not ground - as there 
will be a small ground fault current otherwise.  Might be enough to trip 
off bathroom GFCIs - but only if the meter was installed in certain 
areas of the system which is not likely.  

I think external CT meters will be the long term solution - just need 
less expensive units with bi-directional capability.  

Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com  
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030  

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------





More information about the RE-wrenches mailing list