Charlie,

Of course you're right about the variable voltage not being an issue. The
issue is actually the ultra-conservative stance adopted by many utility
employees regarding inter-connection with a private generator.

Having been a Windmatic ( as well as Bonus, Nordtank, and others) dealer at
one time I think you summed it up pretty well! Don't forget slippery ladders
and squealing brakes.

Cheers,

Matt T
----- Original Message ----- 
From: "Charlie Robb, Element Engineering" <ckr at elementengineering.com>
To: "RE Wrenches" <RE-wrenches at topica.com>
Sent: Thursday, October 23, 2003 5:19 AM
Subject: Re: Combining Turbine Outputs? [RE-wrenches]


> Hang on a minute folks, this is standard "windfarm" stuff you are talking
> about here. The turbines can all be connected direct to a single
three-phase
> cable, daisy-chained in at their incoming breakers. You don't have to
worry
> about wild a.c. or anything that applies to small battery charging
machines;
> with induction generators the turbines' output frequencies are fixed by
the
> grid, not by the turbines. Each turbine operates independently of the
others
> as a grid connected generator and there should be no control system issues
> with running multiple turbines.
>
> If appropriate (it is often done), the grid can be connected at higher
> voltage to a transformer near the first turbine, and then the windfarm
> distribution may be done at 480V. The issues of selection and protection
of
> cables,
> switchgear etc should be handled by a HV distribution/protection
specialist,
> and the utility should be involved at an early stage.
>
> Often the turbine manufacturers (if still in business) will be able to
> advise on suitable
> arrangements. If you are considering buying used Windmatics, first go
> outside on a windy day and get someone to throw buckets of oily water at
you
> while stamping on your hands with greasy boots. Then post me your wallet
and
> enjoy your last free weekend. If I can help at all at this distance please
> get in touch!
>
> Cheers
> Charlie
>
> Charlie Robb
> Element Engineering
>
> 77 Society Road
> South Queensferry
> Edinburgh
> EH30 9XP      UK
>
> Tel: 0131 331 5835
> Fax: 0131 331 5848
> Mobile: 07887 991866
>
> "Disclaimer:
>
> This e-mail is intended only for the addressee and may contain
> information that is confidential or privileged.  If you are not the
> intended recipient you must not use, disclose, distribute, copy, print
> or rely on this e-mail.  If an addressing or transmission error has
> misdirected this e-mail, please notify the author by replying to this
> e-mail."
>
> ----- Original Message -----
> From: "David Blecker" <blecker at seventhgenergy.org>
> To: "RE-wrenches-topica.com" <RE-wrenches at topica.com>
> Sent: Wednesday, October 22, 2003 2:52 PM
> Subject: Combining Turbine Outputs? [RE-wrenches]
>
>
> > Windy's et al,
> >
> > I'm working on the design of a 3 wind turbine project.  Each turbine is
> > 65kW at 480V, 3-phase, 200 Amps max.  The machines will be located about
> > 700 feet from the point of interconnection (POI) and rather than bring 3
> > sets of parallel cables back to the POI, I'm thinking that it would be
> more
> > economical to combine their outputs in the field and run a single set of
> > cables back to the POI.
> >
> > Does anyone have a suggestion on what type of equipment is available to
> > establish a code-compliant 3 into 1 combiner bus? I'm imagining some
kind
> > of pad-mounted NEMA enclosure, but quite frankly, this is bigger than
> > anything I've ever done and I'm quite clueless about the options.
> >
> > Thanks to all,
> > Dave
> >
> >
> > ----------------------------------------------------------
> > David Blecker, P.E., Director
> > Seventh Generation Energy Systems
> > 608-424-1870 (ph)  424-1810 (fax)
> >
> > - - - -
> > To send a message: RE-wrenches at topica.com
> >
> > Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
> >
> > List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
> >
> > Check out participant bios: www.mrsharkey.com/wrenches/index.html
> >
> > Hosted by Home Power magazine
> >
> > Moderator: michael.welch at homepower.com
> >
> >
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------







More information about the RE-wrenches mailing list