At 11:44 PM -0500 7/1/03, John Blittersdorf, Cent. VT Solar & Wind wrote:
>
>    Which brings up another odd situation I had.  A Honda 5000 watt generator
>feeding a DR1524 suddenly started kicking the ground fault breaker on the
>generator after working fine for months.  I had not broken the ground/neutral
>in that generator and had not grounded the generator.

The system neutral should only be grounded at one point in the 
system.  If it is grounded at the generator as well as the inverter 
(say) then current will flow in the grounding conductor between the 
two points.  This will trip any ground fault interrupt which you fit 
between the two.
-- 
Hugh

An unprovoked attack by one nation on a another nation is terrorism. 
'Liberation' applies only with consent of the liberated parties, and 
with respect for innocent lives (of whatever race).
hugh at scoraigwind.co.uk
http://www.scoraigwind.co.uk/

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================


</x-flowed>



More information about the RE-wrenches mailing list