Wow!  Ray, does your pile include the SW4048/24 as well with its
respective/relative surge capacity?

PD
ASAP POWER!

-----Original Message-----
From: Ray Walters [mailto:remotech at taosnm.com]
Sent: Wednesday, October 01, 2003 7:03 PM
To: RE-wrenches at topica.com
Subject: RE: Well pumps and SWs revisited [RE-wrenches]


NO one has mentioned in this thread that the SW5548 is terrible at surges.
I've been disappointed that it trips its over current switch when a lowly
DR2424 can hang in there.( on air compressors for example) This has been
covered on the list before.
I've run a 2 hp pump with a T240 and DR3624 before in an emergency. It
started and stopped flawlessly even at 350 ft and 40 psi in the pressure
tank.
I  put the SW5548 in the same pile as the PS series ,XTR sun tie etc. I
won't sell em!

Ray

At 06:54 AM 10/1/2003 -0700, you wrote:
>I recently installed a SQ 1/2 hp two wire and it starts flawlessly on
>the VFX inverter I am currently running. Really does not have any surge
>to speak of starts at low current and ramps up.  Lovely thing.
>
>Ezra
>
>-----Original Message-----
>From: Jay Peltz, Peltz Power [mailto:jay at asis.com]
>Sent: Tuesday, September 30, 2003 9:07 AM
>To: RE-wrenches at topica.com
>Subject: Re: Well pumps and SWs revisited [RE-wrenches]
>
>
>Hi Ken,
>
>If you are looking for a pump answer then go with a Grundfos SQ pump.
>They come in 240 and have no surge, therefor they work great especailly
>with those 5548's.
>
>jay
>
>Peltz Power
>----- Original Message -----
>From: "Ken Hulet, Engineering Services Co." <esco at revolutionearth.com>
>To: "RE wrenches topica.com" <RE-wrenches at topica.com>
>Sent: Tuesday, September 30, 2003 5:27 AM
>Subject: Well pumps and SWs revisited [RE-wrenches]
>
>
> > I know this has been beaten to death but I got a call a year ago about
>
> > a potential PV install. The owner was building and so we went through
> > some of the basics. You know, 115V well pump if possible and if not,
> > smaller and efficient. I never hear from the guy until... months later
>
> > we get to put in a SW 5548 system. I'm concerned about the pump
> > because the well pump installer laughed when our customer mentioned a
> > 115V pump.
> >
> > We put in the T-240 and learned the pump is a 1.5HP, TWO wire and
> > SURPRISE the 5548 trips on high current when the well pump calls for
> > power. Using a Fluke clamp on I measured 29.7A inrush (100ms) on one
> > of the 230V lines when using the generator to power the pump.
> >
> > Any retrofit/improvement ideas or are we looking for a new pump?
> >
> >
> > Ken & Chris Hulet
> > Engineering Services Co.
> > P.O. Box 4
> > Blanchardville, WI 53516
> >
> > 608.523.3726
> >
> > http://www.revolutionearth.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------






More information about the RE-wrenches mailing list