Need help with grounding problem [RE-wrenches]
Hugh Piggott
hugh at scoraigwind.co.uk
Sun Jul 20 07:58:00 PDT 2003
<x-flowed>
hi
> Neutral wire is bonded at
>tower location at one point to ground rod system. ...At the
>residence the circuit
>breaker panel is also grounded to the neutral by
>connecting to the 240' well casing.
That's a mistake. Keep the grounding system completely separate from
teh neutral except for one bonding connection at the service panel.
--
Hugh