Need help with grounding problem [RE-wrenches]
Doug Pratt
dmpratt at sbcglobal.net
Sun Jul 20 11:28:44 PDT 2003
> Neutral wire is bonded at
>tower location at one point to ground rod system. ...At the
>residence the circuit
>breaker panel is also grounded to the neutral by
>connecting to the 240' well casing.
That's a mistake. Keep the grounding system completely separate from
teh neutral except for one bonding connection at the service panel.
--
Hugh
AND!...the grounding system at the tower needs to be bonded to the
grounding system at the house. Preferably with a bare copper wire that's
buried directly, *NOT* in conduit. Multiple grounding points in a single
system are fine, so long as they're all bonded together. Is this a guyed
tower? You should have a ground rod on each guy wire anchor, then all
bonded together, and bonded back to the house ground.
-Doug Pratt
--^----------------------------------------------------------------
- - - -