Anemometer Options [RE-wrenches]
David Blittersdorf
davidb at nrgsystems.com
Mon Feb 18 14:01:59 PST 2002
Question for Logan,
I have a Gridtek inverter on my 10kw and was having problems with bus overvoltage
faults. I talked with Ken Craig at Bergey and he suggested that there were problems
with high voltage on the utility side that causes these problems. I have 244 -248 VAC on
my AC side most of the time. It goes higher at night with lightly loaded distribution lines.
I added a buck/boost transformer (500 watt, 12-24/120-240) and lowered the voltage to
the inverter by 12 volts and now it doesn't trip offline. I reset my inverter 6 times one
night between 1 and 6 am and I was really annoyed and grumpy the next day and
wanted it fixed.
Is this the types of problems you were having?
David
On 18 Feb 2002 at 10:56, John Raynes wrote:
> >We have used Onset's Hobo loggers to troubleshoot Trace Gridtek-10
> inverters with great results.
> Hey Logan, What types of sensors or inputs were you monitoring with the
> Hobo when you were troubleshooting the Gridtek units? I'm curious.
David Blittersdorf
NRG Systems, Inc.
110 Commerce Street
Hinesburg, VT 05461 USA
Tel: 802-482-2255
Fax: 802-482-2272
email: davidb at nrgsystems.com
Web:http://www.nrgsystems.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list