end battery failure? [RE-wrenches]
Jay Peltz, Peltz Power
jay at asis.com
Tue Dec 17 21:06:01 PST 2002
Hi all,
Here is another battery question.
48v battery, L-16's, 2 strings. Batteries on good system, hydro all winter, good
summer sun, pretty well maintained, desulfaters as well. 2 x 4048 inverters, 15kw
genset.
One both strings, the end batteries failed, while all the interior ones are fine.
One comment ( clue), the owner likes to keep the batteries very high, 60v. Now
this isn't a problem in the summer, but in hydro weather, this could mean 60v for
days or even weeks at a time.?
Thanks all,
jay
Peltz Power
- - - -