Hi Steve,

I've used a bunch of the C-40's as diversion load controllers and I like them
better than the enermaxer.

The enermaxer only has one voltage, isn't conduit ready, can't auto eq, and cost
way more than the C-40's.

I would put only one into auto EQ mode.  I find also that they will compete a
little with voltage, but if the bulk and float voltages are where you want them,
isn't it OK that once in a while they are out of sinc with each other?

Personally if you are just burning the energy as heat, then, much easier to use
one CC mode for the PV, and then go with the other for diversion load.

And don't you love the regs that state that you have to have load sized at 120%
or something of the controllers rating.  Which means that the controller can
fail as its trying to power something to large!

See ya,

jay

"Steve Willey, Backwoods Solar" wrote:

> Well, no, not 4 control units. It will, just have 2 units anyway. Just
> toying with one carrying 80% of load as series solar, the other carrying
> balance as diversion to handle the small seasonal hydro and overflow solar.
> Not true back-up that way. Or could make two diversion controls and shut off
> auto-equalize and balance them with at least fairly close settings
> Steve Willey       steve at backwoodssolar.com
>
> ----- Original Message -----
> From: "Jeff Clearwater, Ecovillage Design" <clrwater at earthlink.net>
> To: <RE-wrenches at topica.com>
> Sent: Friday, September 13, 2002 2:26 PM
> Subject: Re: Diversion charge control [RE-wrenches]
>
> > Hi Steve,
> >
> > Why not use an Enermaxer that's rated at 60 amps @ 48 Volts.  They do
> > buzz (audibly and well as electrical noise) but they are robust and
> > simple.  Equalization is manual is only drawback.  The backup unit
> > you can just set at a little higher voltage and it won't interfere.
> >
> > That way you'ld have 2 units instead of 4! if you need parallel and
> > redundancy at that amperage.
> >
> > Jeff Clearwater
> > Ecovillage Design
> >
> >
> > >I understand the code is requiring diversion type charge controls to be
> > >redundant as back-up for safety in case a dump load burns-out.I am
> currently
> > >specifying a system that will need TWO Trace C-40 controls because
> combined
> > >PV and seasonal hydro will total about 51 amps at 48 volts. (48 volts
> means
> > >C-60 cannot be used).
> > >
> > >While I have used C-40 in solar series control mode side by side for two
> 30
> > >amp arrays, I have concerns bout their function as diversion.  In series,
> > >when one drops to float mode, the other can carry on just fine, holding
> > >until it also reaches requirements for going to float. The other control
> and
> > >array may till hold battery voltage up at bulk  They can even equalize
> > >automatically at different times if their portion of the charge source is
> so
> > >capable.
> > >
> > >However, set up as a diversion control, when one goes to float mode it
> will
> > >probably pull the battery down so that the other never will go to float.
> > >Automatic equalization would never happen so long as one control might be
> > >pulling for float while the other tries to equalize.  Any experience in
> > >setting these up and how they work together or not? One option being
> > >considered is one control as diversion and most of the solar processed
> > >series through the other. But part of the problem may remain where the
> > >diversion unit can pull everything toward float voltage, taking most of
> the
> > >load most of the time.
> > >
> > >Steve Willey       steve at backwoodssolar.com
> > >www.backwoodssolar.com
> > >Backwoods Solar Electric Systems
> > >Home electricity from sunlight for
> > >locations with no utility lines.
> > >Free instructional catalog.
> > >----- Original Message -----
> > >From: "Bill Brooks" <billb at endecon.com>
> > >To: <RE-wrenches at topica.com>
> > >Sent: Thursday, September 12, 2002 9:53 AM
> > >Subject: RE: SPAM: Data missing from SP140 cut sheet [RE-wrenches]
> > >
> > >
> > >>  William,
> > >>
> > >>  Here is the information you seek. I share your frustration. Many
> companies
> > >>  are poor about providing basic information like this.
> > >>
> > >>  Model Vmp Imp Voc Isc
> > >>  SP140-24P 33 4.25 42.8 4.7
> > >>  SP150-24P 33 4.4 43.4 4.8
> > >>
> > >>  Bill.
> > >>
> > >>
> > >>  -----Original Message-----
> > >>  From: William Miller [mailto:wrmiller at slonet.org]
> > >>  Sent: Wednesday, September 11, 2002 9:29 PM
> > >>  To: solarinfo at si.shell.com
> > >>  Cc: RE-wrenches at topica.com
> > >>  Subject: SPAM: Data missing from SP140 cut sheet [RE-wrenches]
> > >>
> > >>
> > >>  Dear Sirs or Ms:
> > >>
> > >>  I just downloaded the 2 page cut sheets for the Shell SP140 and SP150
> PV
> > >>  modules.  There is at least one item of data glaringly absent:  The
> rated
> > >>  output current.  This was listed for all Siemens products but has
> > >>  apparently been left out of the documents redone by Shell.  The
> documents
> > >>  in question are:  ShellSolarSP140_UKv5.pdf and
> ShellSolarSP150_UKv5.pdf.
> > >>  For an example of a correct document, please see the Siemens cut sheet
> for
> > >>  the SP150.  It does contain the rated amperage.
> > >>
> > >>  I must emphasize that designers and field installers must have access
> to
> > >>  published data in order to file complete design documents and building
> > >>  permit applications.  This is an important part of manufacturers
> support.
> > >>
> > >>  Please correct the documents cited and e-mail them to me at this
> e-mail
> > >>  address at your earliest convenience.  Thank you in advance for your
> > >>  assistance.
> > >>
> > >>  Sincerely,
> > >>
> > >>
> > >>  William Miller
> > >>
> > >>  PS:  If I may, I'd also like to suggest that these documents contain a
> > >>  minimum of color for ease in printing in standard office color
> printers.
> > >>  We need to print multiple copies of these cut sheets and it really
> > >consumes
> > >>  a lot of color ink if the sheets are too busy with color.
> > >  >
> > >>  Thanks,
> > >>
> > >>  WM
> > >>
> > >>  __________________________________________________________________
> > >>  William Miller
> > >>  Miller Power and Communications
> > >>  PO Box 50, Santa Margarita, CA 93453
> > >>  Voice :805-438-5600 Fax: 805-438-4607 VMail: 805-546-4875
> > >>  email: wrmiller at slonet.org
> > >>  http://millerpowerandcomm.com
> > >>  License No. C-10-773985
> > >>  _____________________________________________________________
> > >>  Compatibility:
> > >>  Word processor: WP7
> > >>  Spreadsheet: Quatro Pro 7
> > >>  CAD: Microstation 95, DXF, Visio 4.1T
> > >>  _____________________________________________________________
> > >>  "Every decent man is ashamed of the government he lives under."
> > >>                                      H. L. Mencken
> > >>  __________________________________________________________________
> > >>
> > >>  - - - -
> > >>  To send a message: RE-wrenches at topica.com
> > >>
> > >>  Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
> > >>
> > >>  List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
> > >>
> > >>  Check out participant bios: www.mrsharkey.com/wrenches/index.html
> > >>
> > >>  Hosted by Home Power magazine
> > >>
> > >>  Moderator: michael.welch at homepower.com
> > >>
> > >>  - - - -
> > >>  To send a message: RE-wrenches at topica.com
> > >>
> > >>  Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
> > >>
> > >>  List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
> > >>
> > >>  Check out participant bios: www.mrsharkey.com/wrenches/index.html
> > >>
> > >>  Hosted by Home Power magazine
> > >>
> > >>  Moderator: michael.welch at homepower.com
> > >>
> > >>
> > >>
> > >>
> > >>
> > >>
> > >>
> > >>
> > >
> > >- - - -
> > >To send a message: RE-wrenches at topica.com
> > >
> > >Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
> > >
> > >List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
> > >
> > >Check out participant bios: www.mrsharkey.com/wrenches/index.html
> > >
> > >Hosted by Home Power magazine
> > >
> > >Moderator: michael.welch at homepower.com
> > >
> >
> > --
> > ~~~~~~~~~~~~~~~~~~~
> > Jeff Clearwater
> > Ecovillage Design Associates
> > Home, Community and Village Scale Renewable Energy Systems
> >
> > 2525 Arapahoe Ave, Suite E4, #280
> > Boulder, CO 80302
> > 1-800-440-2523 PIN7071
> > Fax:  720-528-7813
> > clrwater at earthlink.net
> > jeffc at ic.org
> >
> > Council Member - Ecovillage Network of the Americas -
> http://www.ecovillage.org
> > Founder:  Ecovillage Research, Development, and Demonstration Program:
> > http://www.home.earthlink.net/~clrwater/RDD/rdd.html
> > ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
> >
> > - - - -
> > To send a message: RE-wrenches at topica.com
> >
> > Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
> >
> > List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
> >
> > Check out participant bios: www.mrsharkey.com/wrenches/index.html
> >
> > Hosted by Home Power magazine
> >
> > Moderator: michael.welch at homepower.com
> >
> >
> >
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================





More information about the RE-wrenches mailing list