Hypalon Cable [RE-wrenches]
Bill Brooks
billb at endecon.com
Tue Jul 23 09:07:30 PDT 2002
Bob-O,
As we put this issue to rest, in my mind it has far more to do with keeping
things simple for the inspectors than it does politics. Our current battery
systems are far too complex for inspectors to know whether the right
batteries are being used and the right conductors, and overcurrent
protection, and trays, and enclosures, and ventilation, and..., and.... This
is not a good situation at all. Inspectors hate it because they now have to
figure out whether you are a good wrench and know what you are doing, or
whether you are a moron and now have put the home and the owner at risk.
Ultimately we need fully listed battery systems (very soon) if we are going
to get to the point of broad acceptance and the type of even treatment we
want from our building officials. Outback Power and Xantrex seem to be
breaking some ground in this area and it is about time. The inspector would
like to be able to look at a battery system, see the ETL label on the side
showing that it is a listed system, and then all they need to inspect is
that the system is installed according to the directions. All the conductors
(or busbars or uninsulated cable, or welding cable) , and overcurrent
protection are part of the system. That is my goal and until we get there we
are going to be farting around with these less significant issues for years
to come. I'm done.
Bill.
-----Original Message-----
From: Bob-O Schultze, Electron Connection
[mailto:econnect at snowcrest.net]
Sent: Tuesday, July 23, 2002 7:32 AM
To: RE-wrenches at topica.com
Subject: RE: Hypalon Cable [RE-wrenches]
Bill,
Of course the NFPA who is totally and incestuously abed with UL is
not going to change their mind on welding cable. What WE all need to
realize is that it has far more to do with politics than safety,
which is driving that decision. When I say we Bill, I mean you too.
Your inspector seminars and course book stress in the strongest terms
that non-UL cable for batteries is unacceptable. Nothing in your talk
modifies that with a dose of field reality in any way. That stance,
as much as the NFPA's, is what will keep the cost of an RE system
beyond the grasp of some for many years. If you're not part of the
solution.....
Bob-O
>Having seen this installation I can tell you the wire was not abused. No
>amount of discussion will sway the code making panel on this issue, so we
>look for other issues that need more attention and have a greater impact.
>I'm done on this issue and I wish Drake the best with his proposal. If I
>were a better person (which I'm not) I would be willing to bet that the
>proposal for welding cable will not succeed because they will point out
that
>the code already has a very well-defined wire marking system and something
>listed as welding cable alone cannot possibly cover the testing
requirements
>for batteries and conduit. Whether you agree with Drake or not will not
>change the reality. The NEC is not an existential document no matter how
>much we may want it to be.
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list