Back-fed Circuit Breakers [RE-wrenches]
Matt Lafferty
pvpro at attbi.com
Sat Feb 9 08:30:34 PST 2002
EH and others:
The easiest way I've found to deal with this issue is simple. First section
in the NEC. Right up front, in plain English.
As Bill Brooks has already stated, a "hold-down" is necessary in a battery
backup situation.
In a purely grid-tied installation, however, the AC circuit is purely an
Individual Branch Circuit per NEC 100. (As with all code books, it is
listed as "Branch Circuit, Individual".) I have demonstrated the "drop-out"
to a number of inspectors in the field and reassured them that there are no
"back-up" provisions.
I did have one sharp inspector question "What's the load, if it's a branch
circuit?". My response to him was, "When the sun goes down, the inverter is
the load". He's satisfied. (I know, John B, not much of a load)
To date (over 100 such installs) the Branch Circuit answer has resolved it
every time.
Pray for Sunshine,
Matt Lafferty
PS - If the panel is that old, an upgrade would be appropriate!
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list