Back-fed Circuit Breakers [RE-wrenches]
Kent Sheldon
kentsheldon at sbcglobal.net
Fri Feb 8 15:22:32 PST 2002
I thought I was going nuts, but I think EH meant 384.16(f) in NEC 1999,
and the 2002 NEC has shuffled everything around. It is now 408.16(f).
____________________________________________
Kent Sheldon
Manager, Industrial Power Systems
SMA America
kent.sheldon at sma-america.com
925 513 8813 Brentwood Office (Primary)
530 273 4848 Grass Valley Office
-----Original Message-----
From: EH Roy [mailto:ehroy at solar-works.com]
Sent: Friday, February 08, 2002 1:39 PM
To: RE-wrenches at topica.com
Subject: Back-fed Circuit Breakers [RE-wrenches]
On grid-interactive residential PV systems, I am finding that utility
inspectors are starting to insist on retainer kits for back-fed breakers
in the home load centers - as required by NEC Article 384-16 Section
(g).
Does anyone have a good solution for older load centers and breakers
(such as Challenger and Wadsworth) that are not manufactured anymore? I
have not been able to find retainer kits for them and sure hope that the
load center and breakers don't have to be replaced.
Thanks for any help or ideas.
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list