>Eric Smiley wrote:
>Some of the breakers like the FA breakers only achieve the factory
>certified 600 VDC rating if you run your positive through all three
>poles of a 3 pole breaker. None of their breakers show a 600 VDC >UL/CSA
>recognition or listing.
OutBack offers a six pole 15 amp circuit breaker which is ETL listed for
up to 600 vdc for PV applications. All of the six pole's trip
mechanisms are internally connected to ensure common operation.
See the OutBack PSSB "Segmenting Breaker" on our website for more
information.
Systems with voltages above 600 VDC are not adviseable due to the
limitations in the NEC.
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com www.outbackpower.com