Trace ST problems [RE-wrenches]
    Eric Smiley 
    Eric_Smiley at bcit.ca
       
    Mon Mar  5 15:19:40 PST 2001
    
    
  
John's post caused a stir here as we are planning on using the ST in the
near future.
Fortunately the ST has a larger MPPT window (42-85 Vdc) than John stated.
>With the MPPT window being only 52 to 85 it is very difficult to find an
>array configuration that it will power track year round.
On paper, it looks like the standard EPV module would be a poor choice for the ST.
I was very surprised that Trace had done field testing with EPV modules and they worked at voltages as low as 40 Volts!
http://www.gridtie.com/support/technicalbriefs/tn3/index.html
I have specs for a standard 40 Watt EPV module and a letter from Alan
Delahoy which gives the voltage temperature coefficient as -0.28%/
degree C.
Vmp = 44.8 volts
Voc = 62.2 volts
At a module temp of -20 C.
Vmp = 44.8 x 1.126 = 50.4 volts
Voc = 62.2 x 1.126 = 70.0 volts
At a module temp of +70 C
Vmp = 44.8 x 0.874 = 39.2 volts|
Voc = 54.4 volts
In other words the SunTie shouldn't work very well with these particular
modules at high temperatures.
We weren't planning on using EPV modules anyways, but perhaps Trace
would like to comment on how they got such exemplary results at such low
voltages?
I have also done the above calculation for four nominal 12 V crystalline modules and Solarex Millenia modules.
They fall within the MPPT window at the above module temperatures.
----------------------------------------------------------------------
Eric Smiley
Project Leader - BCIT Technology Centre
Photovoltaic Energy Applied Research Lab (PEARL) - BCIT
ph: (604)432-8657 www.bcit.ca/~tc/pearl/index.htm
- - - - - - -
To send a message:
 RE-wrenches at topica.com
The archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
 http://www.mrsharkey.com/wrenches/etiquete.htm
To unsubscribe send a message to: 
 RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine: 
 www.homepower.com
For info contact list moderator by email:
 michael.welch at homepower.com
____________________________________________________________
T O P I C A  -- Learn More. Surf Less. 
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
    
    
More information about the RE-wrenches
mailing list