>My question is about transferring loads that may(?) be out of phase.
Kurt;
Yes, this can be a big problem, particularly when inductive loads
(transformers, motors) are involved. If your relay transfers a load from
one phase to another, or from one source which is significantly
out-of-phase with another, you'll end up blowing breakers, frying
contactors, and possibly cooking the equipment as well.
What happens is that any inductive loads will have a magnetic field built
up around the ferrous core/armature. This field will begin to collapse as
soon as the relay disconnects, inducing counter EMF into the AC line. If
the (new) incoming AC is out-of-phase, you'll have *twice* the single-phase
potential across the relay contacts at lots of amps instantaneous. Arc-city
big time!
What you may want to do is use two relays, one for one AC supply, and a
second one for the other. Relays with a built-in time delay are available
from Grainger, etc. You may need to control the large AC contactor with
these smaller relays. Even a .5 second delay before the AC transfer takes
place will be enough for the magnetic flux to collapse and stabilize.
>Question 2? I still can't find a good supplier for 24VDC contactors in
>the 60-100 amp range. What is Trace using for their 60 amp, an open
>framed power relay, or a contactor? Any thoughts?
Trace is using double pole 30 amp enclosed relays with the poles
paralleled. I tend to lean towards solid-state relay devices.
Zero-crossover switching, no contacts to arc or pit, no moving parts,
operate from a variety of DC voltage sources, etc...
-S
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
____________________________________________________________
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
More information about the RE-wrenches
mailing list