The settings for the MNS Batteries are on a sticker on each battery.

BMS- LVCO 44.8 HVCO 58V (The HVCO is not on the sticker)
LVCO (inverter) 46.0
Float 54V
Bulk 56.1V

The rest of the  you can set to what you want, the battery does not care.
All Prismatic cells operate mostly the same, and the MNS Batteries use A+
Automotive cells MFG by EVE.

Thanks

Logan


On Mon, Feb 3, 2025 at 8:47 AM Jay via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Hi Bill
>
> I tried and failed to find any setting information on that battery besides
> charge and float.
> Kinda need to know things like LVD, recommended LBCO, etc.
> But if it’s similar to other prismatic cells you should be able to set the
> OB inverter to a LBCO that works without having to go through a aux relay.
>
> Jay
>
> > On Feb 2, 2025, at 9:53 PM, Bill Battagin via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
> >
> > Have any off-gridders done a system with Powerflo16's to power pre-LFP
> OB/FX inverters?  The FM80's LFP settings in this system are compatible
> with LFP but I'm looking for options other than using the Aux in the CC's
> wired to a NC relay and from there to the inverter on/off landings in the
> green terminal of the OB/FX for the LBCO and reconnect function.
> >
> >             I've been down this road before, though a different
> equipment.  I've used the Aux from a Classic for inverter LBCO and
> reconnect though its never been fully "tested", although I read "open" and
> closed" at the un-wired aux landing when I forced it with a high LBCO
> setting.  Just thinking about the highest reliability.
> >
> >         Thanks in advance.
> >
> > Bill
> >
> > Feather River Solar Electric
> > Bill Battagin, owner
> > 4291 Nelson St. (Shipping)
> > 5575 Genesee Rd. (USPS, UPS)
> > Taylorsville, CA  95983
> > 530-284-7849, 258-1641(cell)
> > CA. C10 Lic # 874049
> > Solar Powered since 1982
> > Home of the Sunny Side Up
> >
> >
> > --
> > This email has been checked for viruses by Avast antivirus software.
> > www.avast.com
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > Pay optional member dues here: http://re-wrenches.org
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > There are two list archives for searching. When one doesn't work, try
> the other:
> > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > http://www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > http://www.members.re-wrenches.org
> >
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20250203/17046160/attachment.htm>


More information about the RE-Wrenches mailing list