[RE-wrenches] Generator overvoltage troubleshoot
Jerry Shafer
jerrysgarage01 at gmail.com
Sat Nov 9 10:48:22 EST 2024
Jim
Is the system set to global, i had seen issues with this setting, some of
what you said also fits.
Fun times
On Fri, Nov 8, 2024, 8:34 PM Jim Gowdy via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Hi all,
> I need some help with a generator overvoltage troubleshoot. I'm
> working on an outback offgrid system that consists of 2 x Radian GS8048a, 1
> x MATE3S controller, 1 x FM 80 charge controller, 1 x 55kw cummins
> generator, about 4kw of solar *not sufficient enough to keep up with the
> load, and 24 x 4v Rolls batteries series/paralleled to make 48v. The
> generator was rebuilt and the batteries replaced about a year ago and since
> then, the generator has been faulting due to overvoltage. I had help and
> first found that the MATE needed calibrating so that was done, but the
> generator still was faulting. I found changing the AC Input Charging from
> 30a to 20a seemed to work. I put a power monitor on the generator output
> and found that, with the AC Input Charging set at 30a, noticed that there
> was a voltage spike up to 300+V at about a 70a draw. The generator company
> put a load bank on and verified the generator may not be at fault and the
> problem is after the generator. Has anyone encountered a problem like this
> and have suggestions?
>
> --
> Jim with Gowdy Electric
> Cambria, Ca 93428
> business 805 927 2630
> cell 805 975 5279
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20241109/03a12831/attachment.htm>
More information about the RE-Wrenches
mailing list