[RE-wrenches] More Issues with Parallel Sol-Ark 15K System

Jason Szumlanski jason at floridasolardesigngroup.com
Sat Nov 9 10:15:39 EST 2024


I wrote in another thread about an off-grid quad Sol-Ark system that was
shutting down due to parallel stop when one of the four inverters
experienced a DC PV fault, and how that shutdown is far from ideal. The
same system is down once again, this time due to an AC fault code.

The homeowner started getting repeated F18 and F34 AC overcurrent faults on
one of the slave inverters. This, in turn, shut the entire system down due
to parallel stop faults (F41). None of the other units had AC
overcurrent faults, and the load is nowhere near requiring all four
inverters for even the most demanding circumstances. It was designed this
way for redundancy, which I am quickly finding out is not Sol-Ark's strong
suit.

To diagnose the issue remotely, I had the owner turn off all four load
breakers, all DC PV input, and the AC microinverter input on the GEN
terminals. I had them restart everything (several times). Every time, the
same inverter would have repeated AC overcurrent faults, and the others
would have parallel system faults. Since there were no loads connected by
virtue of the load breakers being open, I suspected this had to be an
internal fault.

I went to the site, and Sol-Ark Tier 1 tech support had me shut off all
inverters and take the suspect inverter out of parallel operation mode. As
a standalone master it was able to power up and support the entire house
load without issue. Then we reprogrammed it for parallel operation again
and turned everything back on. We were unable to stay on the phone long
enough to determine if this was successful, but ultimately, the fault
returned. I was told to call and ask for Tier 2 next time if it happened
again, which I intend to do on Monday. At this point, the issue can only be
internal to the unit, and I intend to demand warranty replacement of
suspect components or the whole unit.

I had to get the system running, so I wanted to take the bad inverter out
of the parallel system. I was hoping that simply shutting it down would
work. This is the third of 4 inverters in the Modbus chain. When turning it
off completely (all AC and DC switches disconnected), the 4th inverter
would fault, presumably because the Modbus signal was not being relayed,
but inverters #1 and #2 worked fine. However, I wanted #4 to also continue
working while taking #3 out of service. So then I turned on the battery
disconnect for #3 but left it in the off mode by not pressing the on/off
button, thinking that it would allow relay of the Modbus signal from #2 to
#4. That allowed the system to work momentarily, but then everything
faulted out due to parallel system stop. In other words, I was going to
have to physically take #3 out of the Modbus daisy chain to make this work.

Of course, I didn't have a long enough Cat5 cable with me, nor a Cat5
splice connector. So I had to rig something, which I did successfully to
jumper from #2 to #4. But when I turned everything back on, #4 still would
not work. I eventually realized that you have to change the Modbus address
from 04 to 03 in the settings. Apparently, the addresses need to be
sequential for it to work. Once I did this, I was able to get the system up
and running again as a triple-inverter parallel setup. No faults were
observed. So the theory was proven that #3 has an issue internally.


Anyway, bottom line, I am disappointed at how one inverter fault takes down
the whole paralleled system, and also how taking a faulted inverter out of
the system requires physical and programming changes. Turning it off should
be sufficient. This is a very poor way to implement a parallel system that
should provide the peace of mind that redundancy implies. Now I have a
customer who thought they were getting a system with failsafe redundancy
that actually requires a service call every time one of the
paralleled units decides it does not want to play nicely with others.