[RE-wrenches] Outback VFX 2812 charger not working
Steve Higgins
steve at surrette.com
Wed Aug 14 18:26:39 EDT 2024
Michael,
Your AC Relay contacts on the utility side are dead... the AC Relay boards
on the VFX need to be changed out, or you need to pull it and replace the
relay. Those relays have 12 to 14 solder points, so unless you have the
"Jig" for desoldering them, it's a nightmare to replace without it.
You can use the U series to charge like that, but it may not be able to get
the voltage to 2.45vpc to 2.5vpc (14.7 to 15volts), and you may not have
enough current to charge those batteries by itself in a reasonable amount
of time, so do expect long generator runtimes.
You may be able to find one out there. They are pretty easy to replace, but
you have to take extra care not to pinch the two ribbon cables that attach
to them.
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
Steve Higgins ⋅ Technical Services Manager
t +1.902.597.4020 m +1.206.790.5840
f +1.902.597.8447 e steve at surrette.com
<http://www.facebook.com/RollsBattery>
<https://www.youtube.com/user/RollsBattery>
<https://www.youtube.com/RollsBatteryEngineering>
<https://www.youtube.com/RollsBatteryEngineering>
<https://www.youtube.com/RollsBatteryEngineering>
<https://www.linkedin.com/company/rolls-battery-engineering>
<https://www.linkedin.com/company/rolls-battery-engineering>
<https://www.linkedin.com/company/rolls-battery-engineering>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>
------------------------------
CONFIDENTIALITY: The information transmitted herein is intended only for
the addressee and may contain confidential, proprietary and/or privileged
material. Any unauthorized review, distribution or other use of or the
taking of any action in reliance upon this information is prohibited. If
you receive this email in error, please contact the sender and delete or
destroy this message and all copies.
------------------------------
On Wed, Aug 14, 2024 at 3:14 PM Michael Welch via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Wrenches. I am hesitant to post here, since I am not really a Wrench. I
> feel like maybe I can get by with it since I'm so involved with running the
> list. So ...
>
> After many years, my VFX 2812 stopped charging my batteries, but continues
> powering my home.
>
> The VFX 2812 is mounted to a Midnite e-panel, with two PV inputs (MX-60
> and an old Heliotrope CC-60), a FlexNet DC, HUB, and a Mate2. A battery
> temp sensor is between two of my Surrette 2-KS-33P batteries.
>
> Some time ago, the red error light behind the clear cover on the inverter
> started blinking, but it continued charging from our 7 kW generator -- so I
> suspect it had nothing to do with my current charging problem. Discussing
> with Bill Battagin, the light was possibly a fan error, apparently a bit
> common.
>
> I tried switching generators, as the first one showed 64 CPS, but that did
> not help.
> When I start the generator, the AC In light on the Mate2 on (and stays
> on), and I hear an inverter relay clicking as if the generator warm-up
> delay feature keeps going through its cycle. The house lights flicker at
> the same time as the click, but charging never happens.
>
> I've re-seated all the Cat-5 cables with Outback contact goop on all ends,
> and I replaced the Mate2 cable with a new Outback one. I've checked and
> tightened all the connections in the e-Panel and batteries.
>
> Question 1:
> So what can I do to further diagnose or even fix this? Buying a new or
> even used VFX inverter is out of the question, financially.
>
> Question 2:
> I still have my old Trace U2512 inverter. I'd like to hook its charger
> into the e-Panel, as a temporary situation -- for times like last week
> when we were fogged in for a few days, letting my batteries get a lot lower
> than I want.
>
> I would not use the AC output on the Trace, but would continue powering my
> home with the VFX. I figured I would put the Trace battery cables in
> parallel with the VFX so that the Trace charging will also go through the
> shunt so I can see the charge rates and levels on the Mate2.
>
> The generator's wires would be changed from the e-Panel AC In to the
> Trace AC In.
>
> The last thing I want to do is further harm my equipment. What say ye to
> this temporary idea?
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240814/42f7af49/attachment.htm>
More information about the RE-Wrenches
mailing list