New AC board [if available) is around $250 +/- and relatively straightforward to replace.
FET board is twice as much $
Sent from my iPad
> On Aug 14, 2024, at 6:19 PM, jay via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>
> HI Michael,
>
> I’d say the AC board on the VFX is suspect. Bad relay.
>
>
> Yes to #2. That will work just fine.
> Good luck
>
> jay
>
>> On Aug 14, 2024, at 4:13 PM, Michael Welch via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>>
>> Wrenches. I am hesitant to post here, since I am not really a Wrench. I feel like maybe I can get by with it since I'm so involved with running the list. So ...
>>
>> After many years, my VFX 2812 stopped charging my batteries, but continues powering my home.
>>
>> The VFX 2812 is mounted to a Midnite e-panel, with two PV inputs (MX-60 and an old Heliotrope CC-60), a FlexNet DC, HUB, and a Mate2. A battery temp sensor is between two of my Surrette 2-KS-33P batteries.
>>
>> Some time ago, the red error light behind the clear cover on the inverter started blinking, but it continued charging from our 7 kW generator -- so I suspect it had nothing to do with my current charging problem. Discussing with Bill Battagin, the light was possibly a fan error, apparently a bit common.
>>
>> I tried switching generators, as the first one showed 64 CPS, but that did not help.
>> When I start the generator, the AC In light on the Mate2 on (and stays on), and I hear an inverter relay clicking as if the generator warm-up delay feature keeps going through its cycle. The house lights flicker at the same time as the click, but charging never happens.
>>
>> I've re-seated all the Cat-5 cables with Outback contact goop on all ends, and I replaced the Mate2 cable with a new Outback one. I've checked and tightened all the connections in the e-Panel and batteries.
>>
>> Question 1:
>> So what can I do to further diagnose or even fix this? Buying a new or even used VFX inverter is out of the question, financially.
>>
>> Question 2:
>> I still have my old Trace U2512 inverter. I'd like to hook its charger into the e-Panel, as a temporary situation -- for times like last week when we were fogged in for a few days, letting my batteries get a lot lower than I want.
>>
>> I would not use the AC output on the Trace, but would continue powering my home with the VFX. I figured I would put the Trace battery cables in parallel with the VFX so that the Trace charging will also go through the shunt so I can see the charge rates and levels on the Mate2.
>>
>> The generator's wires would be changed from the e-Panel AC In to the Trace AC In.
>>
>> The last thing I want to do is further harm my equipment. What say ye to this temporary idea?
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
More information about the RE-Wrenches
mailing list