[RE-wrenches] AC V DC RE: electrolysis

Nick Lucchese lucchesesolar at gmail.com
Fri Jun 21 01:43:20 EDT 2024


Greetings Mac,
Have you personally had success with this by chance? I inherited
maintenance of a system for a friend whose original installer went out of
business and this was their original approach as well however they and they
had used the 100 amp version (even though the system produces just 24
amps). When I originally inspected 3 years ago the system was fine but the
SMM failed last fall and the homeowner missed out on a few months of
production before noticing. Since this was the first time I had come across
this combo I reached out to Generac for approval and two
different technical support departments seemed puzzled it was used for this
purpose and advised against it. I'm now seeking a similar solution like
William but replacing the SMM with a new one sure would make my life
easier. Couldn't really tell if I was speaking to new employees at Generac
and they just weren't willing to look into it deeper or if it's truly a bad
equipment pairing. Looks like it worked for about 5 years before failing
and I was able to determine the failure occurred the last time the
generator had ran during a grid outage. Another local electrician had said
there had been a bad run of the SMM's which adds additional justification
to perhaps try it out again. If you've used the SMM's for this purpose have
you used the 50 as well as the 100 amp version?

Thanks for the input, Nick

On Thu, Jun 20, 2024 at 4:28 AM Mac Lewis via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Hi William,
>
> I don't want to hijack this thread but I want to give you another idea
> for disconnecting the Enphase circuit.
>
> Generac makes a very convenient load shed device called Smart Management
> Module SMM50.  This may be a good option for you.  Instead of having a
> signal wire/trench etc, it is a pass through relay with a board that
> samples the line voltage.  If it senses that the voltage is supplied by a
> generator, you can program it to lock out the load.  You could place it on
> the interconnection of the enphase circuit.  They only guarantee it will
> work with a Generac generator, but I suspect it will work with other brands
> as well.  This could be worth considering.
>
> Good luck!
>
>
>
> On Thu, Jun 20, 2024 at 12:35 AM William Miller via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Friends:
>>
>>
>>
>> I have an installation of 12 Enphase IQ inverters that is downstream from
>> a generator transfer switch.  During power outages the generator will run
>> poorly when the Enphase is on and the sun is shining.  The problems go away
>> when the Enphase is shut off.  No surprises about this.
>>
>>
>>
>> The Enphase is installed on a barn about 150 conduit feet from the
>> generator transfer switch.  My plan is to create a low voltage signal when
>> the generator is running and send it to a coil on a contactor in the barn.
>> Said contactor will disconnect the 12 micro-inverters.
>>
>>
>>
>> There is existing one 26 AWG pairs of a Cat 6 cable running between the
>> buildings.  I have found a two pole, 30A contactor that draws 7 watts on
>> the coil.  The voltage drop calcs on 150 feet of 26 AWG wire shows a 24
>> volt signal will not cause excessive voltage drop (~4%).
>>
>>
>>
>> Here is where I am uncertain:  Should I run 24 volts AC or DC?  My
>> concern about DC is if there are any damp connections, electrolysis will
>> occur that might erode the 26 AWG conductors.  We’ve all seen powder where
>> copper used to be.  Is AC less susceptible to electrolysis?  My research
>> has turned up no pertinent conclusions.
>>
>>
>>
>> Thanks in advance.
>>
>>
>>
>> William Miller
>>
>>
>>
>> Miller Solar
>>
>> 17395 Oak Road, Atascadero, CA 93422
>>
>> 805-438-5600
>>
>> www.millersolar.com
>>
>> CA Lic. 773985
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240620/65b9ff57/attachment.htm>


More information about the RE-Wrenches mailing list