Hi William,
I don't want to hijack this thread but I want to give you another idea
for disconnecting the Enphase circuit.
Generac makes a very convenient load shed device called Smart Management
Module SMM50. This may be a good option for you. Instead of having a
signal wire/trench etc, it is a pass through relay with a board that
samples the line voltage. If it senses that the voltage is supplied by a
generator, you can program it to lock out the load. You could place it on
the interconnection of the enphase circuit. They only guarantee it will
work with a Generac generator, but I suspect it will work with other brands
as well. This could be worth considering.
Good luck!
On Thu, Jun 20, 2024 at 12:35 AM William Miller via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Friends:
>
>
>
> I have an installation of 12 Enphase IQ inverters that is downstream from
> a generator transfer switch. During power outages the generator will run
> poorly when the Enphase is on and the sun is shining. The problems go away
> when the Enphase is shut off. No surprises about this.
>
>
>
> The Enphase is installed on a barn about 150 conduit feet from the
> generator transfer switch. My plan is to create a low voltage signal when
> the generator is running and send it to a coil on a contactor in the barn.
> Said contactor will disconnect the 12 micro-inverters.
>
>
>
> There is existing one 26 AWG pairs of a Cat 6 cable running between the
> buildings. I have found a two pole, 30A contactor that draws 7 watts on
> the coil. The voltage drop calcs on 150 feet of 26 AWG wire shows a 24
> volt signal will not cause excessive voltage drop (~4%).
>
>
>
> Here is where I am uncertain: Should I run 24 volts AC or DC? My concern
> about DC is if there are any damp connections, electrolysis will occur that
> might erode the 26 AWG conductors. We’ve all seen powder where copper used
> to be. Is AC less susceptible to electrolysis? My research has turned up
> no pertinent conclusions.
>
>
>
> Thanks in advance.
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
Mac Lewis
*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240620/a067b667/attachment.htm>
More information about the RE-Wrenches
mailing list