Hi Mac;

I've used the aux control on charge controllers to turn on/off the FX 
inverters, just as you planned.  Works fine, and solves the LBCO 
programming issue.

Now, if someone from the manufacturing side could PLEASE explain why 
they limited the LBCO on all these inverter models. Absolutely makes no 
sense.  Schneider, Outback, even Magnum is too low.......?

Ray Walters


On 7/11/2023 6:19 PM, Mac Lewis via RE-wrenches wrote:
> Hello Wrenches,
>
> I'm trying to solve an issue with an older Outback FX system.  It's a 
> quad stack of Outback 3648 FX inverters and he has a couple of 
> Fortress eVault and an unreliable generator. The LBCO setting can't go 
> high enough to cut out before the eVaults cut out so he 
> occasionally will have to direct charge the eVault to get things 
> running again.
>
> I'd like to use a 12V Aux relay logic to trip the primary inverter 
> on/off contacts before we go into battery shutdown so the solar has a 
> chance to recover the system.  Pretty simple overall but I wanted to 
> see if there are any known ill effects of doing this with substantial 
> load on the system.  Of course, I can use a power relay but this may 
> be better.
>
> Thanks for your input!
>
> -- 
>
>
>
> Mac Lewis
>
> *
>
> "Yo solo sé que no sé nada." -Sócrates
>
> *
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230713/03fdf8fa/attachment.htm>


More information about the RE-Wrenches mailing list