Mac,
I think you've got an elegant solution to the problem. All you need is
an inexpensive relay and to program the Aux output for loadshed. I
believe shutting down the inverter with the remote on/off contacts is
actually less stressful on the inverter than opening a relay or
contactor on the load side.
Kent Osterberg
Blue Mountain Solar
On 7/11/2023 5:19 PM, Mac Lewis via RE-wrenches wrote:
> Hello Wrenches,
>
> I'm trying to solve an issue with an older Outback FX system. It's a
> quad stack of Outback 3648 FX inverters and he has a couple of
> Fortress eVault and an unreliable generator. The LBCO setting can't go
> high enough to cut out before the eVaults cut out so he
> occasionally will have to direct charge the eVault to get things
> running again.
>
> I'd like to use a 12V Aux relay logic to trip the primary inverter
> on/off contacts before we go into battery shutdown so the solar has a
> chance to recover the system. Pretty simple overall but I wanted to
> see if there are any known ill effects of doing this with substantial
> load on the system. Of course, I can use a power relay but this may
> be better.
>
> Thanks for your input!
>
> --
>
>
>
> Mac Lewis
>
> *
>
> "Yo solo sé que no sé nada." -Sócrates
>
> *
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230711/c57a6ef6/attachment.htm>
More information about the RE-Wrenches
mailing list