[RE-wrenches] active vs apparent power readings with solar
August Goers
august at luminalt.com
Fri Apr 28 16:16:58 EDT 2023
Hi All - Yea, I'm suspecting some sort of reading / measurement error. The
system has SunPower AC modules with Enphase IQ7 microinverters and I
believe the electrician measured the readings down by the utility meter,
although I'm not certain. You can see from the bottom of the datasheet that
the power factor setting is 1.0 or adjustable between 0.85 inductive or
capacitive.
[image: image.png]
*August Goers*
On Fri, Apr 28, 2023 at 12:20 PM Christopher Warfel via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> I think the power factor will be very close to one for split phase.
> What's the inverter specs say w/r to this? Chris
> On 4/27/2023 5:10 PM, August Goers via RE-wrenches wrote:
>
> Hi Wrenches,
>
> We have a residential site with grid tied solar where there is an
> electrician involved who has gotten into taking site readings and thinks
> there is a power factor problem. My gut on it is that there is some sort of
> measurement reading error, and that the power factor should be around 1.
>
> The electrician is using a Fluke 3540FC power monitor and has provided a
> spreadsheet comparing active power to apparent power and calculating power
> factor. See below (you might have to open the image and zoom in to read
> it). This measurement was taken with a PV system running, presumably
> sending some power back to the grid. Note that the phase B active power
> measurement is negative (PV exporting to grid) and that the apparent power
> is positive. This nets in a power factor that is crazy low of 0.05.
>
> Does anyone have experience about whether a meter like this can properly
> measure these readings - maybe there is a setting error or it can't deal
> with negative readings?
>
> [image: image.png]
>
> Best,
>
> August
> Luminalt
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:http://www.members.re-wrenches.org
>
> --
> Christopher Warfel
> ENTECH Engineering, Inc.
> PO Box 871, Block Island, RI 02807
> 401-466-8978
> <http://entech-engineering.com>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230428/d85a9900/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 15663 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230428/d85a9900/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230428/d85a9900/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 81378 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230428/d85a9900/attachment-0001.png>
More information about the RE-Wrenches
mailing list