[RE-wrenches] active vs apparent power readings with solar
Christopher Warfel
cwarfel at entech-engineering.com
Fri Apr 28 15:18:50 EDT 2023
I think the power factor will be very close to one for split phase.
What's the inverter specs say w/r to this? Chris
On 4/27/2023 5:10 PM, August Goers via RE-wrenches wrote:
> Hi Wrenches,
>
> We have a residential site with grid tied solar where there is an
> electrician involved who has gotten into taking site readings and
> thinks there is a power factor problem. My gut on it is that there is
> some sort of measurement reading error, and that the power factor
> should be around 1.
>
> The electrician is using a Fluke 3540FC power monitor and has provided
> a spreadsheet comparing active power to apparent power and calculating
> power factor. See below (you might have to open the image and zoom in
> to read it). This measurement was taken with a PV system running,
> presumably sending some power back to the grid. Note that the phase B
> active power measurement is negative (PV exporting to grid) and that
> the apparent power is positive. This nets in a power factor that is
> crazy low of 0.05.
>
> Does anyone have experience about whether a meter like this can
> properly measure these readings - maybe there is a setting error or it
> can't deal with negative readings?
>
> image.png
>
> Best,
>
> August
> Luminalt
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
--
Christopher Warfel
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
<http://entech-engineering.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230428/99c3be0d/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 15663 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230428/99c3be0d/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230428/99c3be0d/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: cwarfel.vcf
Type: text/vcard
Size: 203 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230428/99c3be0d/attachment.vcf>
More information about the RE-Wrenches
mailing list